Combination boiler - hot water
Messages 1 to 20 of 42.
Help please - we have a worcester 240 combi rsf boiler , we have heating, but the hot water comes on for a minute (or less) and then the boiler switches itself off any suggestions or ideas very welcome Thanks
Discussion Archived
Sounds like the divertor valve isnt working,its a fairly common problem with combi boilers Trevor
Discussion Archived
Regards.....PJ
Discussion Archived
I have a Worcester 240 and have also had problems with it. I haven't had hot water (except in shower, heated differently) for months and now the cold weather is here I really miss it!! I recently put the central heating on and that didn't work either!! (it worked last winter). I know I'll probably have to get a Corgi registered person out to fix it but I wondered if anyone had any ideas about how much that might cost? Many thanks, Dane
Discussion Archived
i have a problem with the worcester 240 combi, the CH works fine, but the DHW starts to make hammer noise after a minuite or so, the header tank (open vented system) gets filled with hot water from the boiler, i think it could be a flow issue, the pump is fine and so is the DHW switch, are their any more likely causes? P.S system pressure is just under 1 bar. Thanks Barry
Discussion Archived
It sounds like the hot water heat exchanger is blocked. You need to replace it or take it out and try to clean it with a descaler such as Sentinal Ferroquest or something equally as strong. Make sure you follow the instructions carefully. Hopefully that should solve yuor problem. Trevor
Discussion Archived
Discussion Archived
Jackie, your's sounds like ignition problems. Does the fan start (whirring noise at the top of the boiler)? Does the clicking noise correspond to sparking at the ignition electrode, viewed through the window with the white cover off?
Discussion Archived
Discussion Archived
Please give more details about the lights, I can't see them from here so try to be unambiguous. eg you say the water is off, does that mean no water at the hot tap, or no water that is hot!!? When we've established the fault I'll TRY to estimate the likely price, though this will depend on which area you live in (CORGI mechanics have mortgages too!).
Discussion Archived
Adverts Currently On Preloved - Place an ad here for free
Discussion Archived
Discussion Archived
Next turn the heating only on, thermostat up, boiler CH temperature to midway. Over a 5 minute period turn the room thermostat up and down 10 times, each time note whether the heating successfully starts or not, then leave it on until the boiler thermostat turns it off. Note the lights, on or off? At no point let anyone turn on a hot tap during this test. Turn the boiler off, what's the pressure now?
Discussion Archived
Discussion Archived
Discussion Archived
Don't worry about the mains light, it's a neon and they often flicker, only if it goes off for more than a couple of seconds should you suspect a supply problem. The demand light not coming on leads me to believe your diverter valve is at fault, maybe it's repairable, maybe not as your symptoms of regular tripping out after running hot water steer me towards thinking the valve is sticking between hot water duty and heating duty intermittantly. This leads to internal overheating of the boiler and subsequent tripping, needing to be reset (by you). Pls confirm the assumed symptoms are (substantially) correct. On this basis you must repair/change the diverter valve. There is also the distinct possibility that your heating system is severely sludged, needing chemical cleaning. As for cost? Which area / town do you live in? What is the GC no. of the boiler? This is on the data plate behind the lift-off white front and is preceeded by "G20" We may have to talk on the phone about this but I'm reluctant to put mine up in public, do you have a hotmail or other account I can send it to for the purposes of talking you through this? I'll be away from the PC from tonight for a couple of days.
Discussion Archived
Discussion Archived
Discussion Archived
Discussion Archived
So for a typical boiler on ground floor, two storey house, the pressure should be 0.5 bar minimum, so 1 bar is perfectly adequate. Don't confuse heating system pressure with domestic hot water pressure - they are not the same and upping the heating pressure will not improve the hot water one iota! If it ain't broke.......etc.
Discussion Archived
Messages 1 to 20 of 42.
Important NoteAll messages are submitted by visitors to this web site, and represent their own personal opinion. They do not necessarily represent the views or opinions of Preloved. You use this information at your own risk. Preloved can not be held responsible for any damages or loss resulting from the use of this site. Please see our Terms and Conditions for more details. |
||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||