Worcester 240 - no hot water

Messages 101 to 120 of 184.

Previous  1  2  3  4  5  6  7  8  9  10  Next >


Worcester 240 - no hot water
10 January 2008, 8:46 AM
Al
Joined 30 Jul 2007
30 posts

Oh OK Cliff, sorry. The bleed valve I found on mine as you look at the heat exchanger on the righthand side slightly on the bottom. You can just get to it with everything in place.

btw, it is a Worchester 240 boiler you have yeah?

Alan.

Worcester 240 - no hot water
10 January 2008, 4:39 PM
Cliff
Joined 6 Apr 2007
8 posts

Hi Alan,
You may be onto something, I have tried what you said, and like you described, there was the bleed nipple.

I have bled the air, had to refill via the loop, bled again and again, so there is no air in the exchanger now.

Fingers crossed that this will do the trick.

Thanks again, I will let you know the result. This will probably be in a couple of days, so that I can monitor the situation.

Many thanks

Cliff

Worcester 240 - no hot water
23 January 2008, 7:00 PM
rosie
Joined 23 Jan 2008
1 posts

i get no hot water from my glow worm combi boiler but the heating is working great any suggestions

Worcester 240 - no hot water
29 January 2008, 1:50 PM
Brian Timmins
Joined 26 Jan 2008
8 posts

good luck with your leaky valves ,we regularly had to change them ,just cos we were silly enough to turn them off lol

Worcester 240 - no hot water
5 February 2008, 11:44 PM
busterfridge
Joined 5 Feb 2008
1 posts

HELP----I have a worcester/bosch 240 rsf combi boiler, hot tap water is intermittently hot (usually cold)!
The radiators are there normal hot temperature, had heat exchanger taken out and flushed,flow switch and temp sensors checked ok, still no better,
BG are hell bent on trying to flog me a new boiler ( £2000+) even though its only 10 years old,
Have had the system powerflushed by BG and a magnaclean fitted but still no improvement,
Has anyone got any suggestions on what the problem might be and a remedy (its doing my head in


Worcester 240 - no hot water
6 February 2008, 10:04 AM
Al
Joined 30 Jul 2007
30 posts

I suggest you read this whole message thread, it will be very useful. Things to check are:
1) Divertor valve diaphragm.
2) Divertor valve itself sticking.

The message thread will tell you how to check, etc.

Alan

Worcester 240 - no hot water
6 February 2008, 11:33 AM
Cliff
Joined 6 Apr 2007
8 posts

Hi Alan, sorry for taking a long time to reply, have tried bleeding the valve as you suggested. I thought it was fixed as on the first 24hrs after doing this it didn't need resetting. But that was the only 24hrs!!!

I have just ordered a new diverter valve as found info elsewhere which suggests this could be not operating properly and causing a problem in the exchanger?

We can but try!!

Thanks again

Cliff

Worcester 240 - no hot water
13 February 2008, 2:02 PM
gs-titan
Joined 22 Oct 2007
6 posts

Hi, Its seems to me if the Hot Water is intermittent (hot and cold) with out heating on is the water to the hot tap hot then, If it is hot and working OK it can't be the Hot Water heat exchanger (There is 2 one for the boiler).
I have been told the hot water one is very difficult to flush out, needs removing and heating up in an oven etc.
If hot water is not hot with heating off it could also be the Diverter Valve, these are easily bought from B.E.S. plumbing on the net about £33 including Delivery, and about an hour or so to fit about 5 fittings.
The Worcester 240 Combi boilers are very hard wearing, mine is 1992/5 and still going strong you just need to check each system out to see which part is not working, (Heating and Hot Water separately), if the rads are hot the boiler must be working OK. Good luck, new boilers on ebay about £400/£500 including delivery. GS

Worcester 240 - no hot water
13 February 2008, 3:05 PM
Elaine
Joined 21 May 2007
7 posts

my water seems to take a long time to come through hot I've had to run the water for a long time before it reaches hot

Worcester 240 - no hot water
28 February 2008, 4:39 PM
ray
Joined 7 Dec 2006
24 posts

Hi all
Just to say I have now fixed my boiler.
I have a brand new diaphragm for sale as i had to replace the whole diverter valve in the end.
One only for purchase here:

http://www.buyme1.co.uk/acatalog/Boiler_Parts.html

I had a constant clicking on and off when using the Central Heating, the boiler would fire up for a few minutes then the clicking would start and the boiler would switch off. Sometimes it would stay on for a few hours, then the clicking would start up and the boiler would switch off. The Hot water was always working fine.

Solution:
Drained the system including heat exchanger
Replaced the whole diverter valve
Filled the system
Bled the rads
Bled the heat exchanger
Fired up the system by putting on the hot tap
Bled the pump
All working spot on now, it seems the old diverter valve was clogged up and sticking which was causing problems with the heat exchanger.
Total time from start to finish was about an hour - I am no plumber.
If your heating is fine but you get no hot water then you should only need to replace the Diaphragm - a 10 minute job.
Hope this helps.

Ray

Adverts Currently On Preloved - Place an ad here for free


FOR SALE
NEW Terracotta Ceramic Floor Tiles
Stevenage, Herts, UK
  FOR SALE
Loft insulation
Rochester, Kent, UK
 
FOR SALE
fiat ulysses R reg
Congleton, Cheshire, UK
  FOR SALE
Loft ladder
Litherland, Merseyside, UK
 
 
[More diy ads...]

Worcester 240 - no hot water
3 March 2008, 10:15 AM
Al
Joined 30 Jul 2007
30 posts

Ray, how did you get on with removing the rear main connection to the diverter valve. I tried, but had to abandon it. However, I have no choice now as I think it is the valve for sure now, thanks.

Alan.

Worcester 240 - no hot water
3 March 2008, 11:09 AM
ray
Joined 7 Dec 2006
24 posts

Al
the valve is basically 2 parts.
There are 2 allen screws located on the top and bottom (on the middle section of the valve)
Unscrew these and the front part will pull out the the rear part.
You should then be able to access the rear part a little easier.

Ray

Worcester 240 - no hot water
4 March 2008, 10:37 AM
MrAK
Joined 4 Mar 2008
5 posts

I have read the whole thread, but wanted to describe my problem to confirm what it is that I need to do.

About 2 months ago my Worcester 240 started to drip from the left side (as you look at it) sometimes it doesn't drip, sometimes it drips as much as 500ml per day.

Yesterday, mid-shower, the hot water suddenly stopped. It still occasionally comes on if I turn a hot tap on full. The dripping from the boiler has also become more constant.

CH is fine, and I do get warm/hot water when the CH is on, which indicates that the water is flowing through the boiler.

From what I can tell on this thread, it is the diaphragm/seals that are the problem, and the dripping is presumably due to damage incurred by a seal somewhere.

Is it worth paying £150 for BG to come out and fix it? or Should I have a go myself? I'm reasonably competent and probably above average with this kind of thing, but I've never tackled a boiler before.

Thanks in advance.

Worcester 240 - no hot water
4 March 2008, 10:51 AM
Al
Joined 30 Jul 2007
30 posts

Mark, the diaphragm is really easy to change and you should be more than capable of doing. Read the threads again and go for it. The diverter is fairly easy, but needs a bit more manipulation in getting it off. My advice would be make sure you have all new washers, seals and some plumbers mate.

Good lick.

Alan.

Worcester 240 - no hot water
4 March 2008, 11:07 AM
ray
Joined 7 Dec 2006
24 posts

Defo have a go yourself mate.
You will need a mixed bag of fibre washers for all the connections on the diverter valve, if you decide to replace it totally.
Even if you change just the diaphragm you will still need a couple of fibre washers, but more importantly you will need a rubber O ring for the expanding coupler which joins the diverter valve to the heat exchanger.
I got a mixed bag from B&Q for £1.08 after every plumbers merchant i tried said that none they had would do the trick, and i would need the whole coupling. I used the small one from the bag and it seals perfect.
Also check the joints near the pressure relief valve for the leak, my system had a small leak and i found that the connection to the pressure relief valve had come loose.
If you remove the side panels and drop the control box you should be able to see a bit more.
Make sure you drain down the system and shut off the pipes.
When bleeding do all the rads, the heat exchanger and also bleed the pump . Worked for me.

Ray



Worcester 240 - no hot water
4 March 2008, 3:45 PM
MrAK
Joined 4 Mar 2008
5 posts

Thanks for the help Al and Ray.

I'm going to B & Q tonight to buy some bits, I'll keep posting my progress here (which is the only forum where I have been able to find a solution to the problem).

If I get out of my depth then I'll just call BG, I'm not bothered about the cost, but I'd like to be able to have a go myself.

I've never drained a system before, so I'll try that a few times before getting down to the repair.

Also, I don't have a manual for my Worcester, are there any diagrams online? I don't know what the pressure relief valve looks like.

Thanks for your help.

Worcester 240 - no hot water
4 March 2008, 3:48 PM
ray
Joined 7 Dec 2006
24 posts

its a valve with a red twisty knob on located right at the back

Worcester 240 - no hot water
5 March 2008, 9:05 AM
Al
Joined 30 Jul 2007
30 posts

Mark, I thought you was after changing the diverter valve?

Alan.

Worcester 240 - no hot water
6 March 2008, 11:45 AM
MrAK
Joined 4 Mar 2008
5 posts

Hi Alan.

It is the diverter valve that I need to replace, or the diaphragm inside of it. I suspect now that the leaking problem is a separate issue.

I drained the heating system, (very easy for those who haven't done it before, it's about 2 paragraphs in the B&Q manual) but realised that this is not what I needed to do, as obviously DHW (except it's not hot) still comes through.

Would it be possible to have a step by step of what it is that I need to do to drain the hot water, and then replace the valve?

I assume that it is something like the following process:

1) Turn off boiler power.
2) Turn off water to boiler (or the water main)
3) Run hot taps until no more water comes through (presumably this means that there is no water in the boiler anymore).
4) Take off diverter valve, replace diaphragm or whole valve.
5) Replace valve.
6) Turn on water to boiler.
7) Turn on boiler power.
8) Run hot taps to pull the water through (hopefully now hot water).

Does that cover everything, or will I blow myself up!

I won't do anything until someone confirms this process (I have to wait for the valve to be delivered anyway).

Thanks again for the help.


Worcester 240 - no hot water
6 March 2008, 11:56 AM
Al
Joined 30 Jul 2007
30 posts

Mark, if you have a boiler manual, it is in there. There are a number of service procedures that you can see, including the changing of the diverter valve.

If not, I ahve one at home and I'll scan it and attached it as a photo if you want here.

Alan.

Messages 101 to 120 of 184.

Previous  1  2  3  4  5  6  7  8  9  10  Next >

 

Important Note

All messages are submitted by visitors to this web site, and represent their own personal opinion. They do not necessarily represent the views or opinions of Preloved.

You use this information at your own risk. Preloved can not be held responsible for any damages or loss resulting from the use of this site. Please see our Terms and Conditions for more details.

Not a member yet?

Why not join the fun for free! Members can sell their stuff completely free of charge, have searches prioritised for their local area, and lots more.

Join for free | Member Log In