As it seems to be a dire emergency, if you go to my website link below and ring me between 6.30 and 7.00pm tonight on the MOBILE phone number, I'll see if I can help wouldn't do this for just anyone you know!!
If you want to add your own question, just click on any 'reply to this message'
Wyn.
On Propane at 37mb it burns 239 grams per hour giving 3.3kw heat output so 25.55 hrs running on butane and almost the same 25.1hrs on propane, you did well to get two days then!!
If you want to add your own question, just click on any 'reply to this message'
We have recently bought a 1989 Abbey caravan. It is our first go at caravaning and we have a few problems in getting things going with the heater. The control panel which has a switch and a dial says 'Caravelle 4' on it. The heater which sticks out through the bottom of the caravan says 'Carver' on it and has a switch at the bottom right which when switched up blows air quietly and when switched down blows air more loudly but neither produce heat. When I switch on the 'Caravelle 4' the green light comes on, the heater tries to ignite, there is a sound like it has ignited, but then shuts off very quickly afterwards. It seems to have several goes at igniting and then the green light just flashes. Having read some of the other posts it seems like it is a common problem. We do not have a manual and would be very grateful if anyone could point me in the right direction as it is quite chilly in there at the moment and the children are desparate to eat diner in there tonight (even though it is sitting on the drive!)
___________________ website: http://www.arcsystems.biz email: [Log in to view email] If you want to add your own question, just click on any 'reply to this message'
Many thanks Richard Adverts Currently On Preloved - Place an ad here for free
___________________ website: http://www.arcsystems.biz email: [Log in to view email] If you want to add your own question, just click on any 'reply to this message'
I have a problem with a carver famaster 5500 turbo, we have just took it out of storage to check everyting is ok while useing heater on mains electric about 15 mins later it triped the 10 amp fuse in the van wether its on 1kw or 2kw it only lasts about that time, ive give it clean cleaned dust off fan checked electricts are secure but same thing happens. it also triped 30 amp fuse in the house. any advice or help will be most welcome. thanks john...
I have a Trumatic s3002 space heater, which I think is also sold as a carver 3000. I has recently developed a fault. After lighting the burner the Piezo ignition stays on IE continues to spark after I have released the button. I have checked the connections that I can get to and the unit by the regulator that seems to operate the ignition seems to be moving freely. Can anyone tell me where the fault lies and how to fix it? Thanks John
If not get back to me.
If you want to add your own question, just click on any 'reply to this message'
Yes though the current Truma 3002 was indeed re-badged in the early 90's as the Carver 3000 and before that the SPL3002 right back into the late 70's The spark is switched electronically so the problem is with the electronic control within the ignition module that contains the battery/batteries, or a connection to it After that then faulty electronics are likely to be the problem, but see if you can buy a new module locally on 'sale or return' or borrow one maybe? so you can test the system because cheap they ain't!! Worst comes to the worst, you can always take the battery out or add a switch maybe?
If you want to add your own question, just click on any 'reply to this message'
thanks for the rapid reply i had it on gas this afternoon (gas works fine ) but it still trips the vans 10amp mcb on gas only with fan running? is this a bigger problem or keep to your advice for now. many thanks john......
I'm on holiday on Thursday until the 16th of March, while I'm away I'm going to try and source a reasonably priced supply of new elements, all going well this will solve this problem once and for all.
If you want to add your own question, just click on any 'reply to this message'
I will try that for the next few days. Have a great holiday thanks john.......
Many thanks for your help on the SBE1800. It all works now - although sadly the hairdryer attachement is nowhere to be found! I have one other little probelm in that the drain off plug on the outside of the Cascade 2 water heater is completely sealed in their. Is the best thing just to drill it out and put another one in there? Many thanks Richard
many thanks
Messages 2521 to 2540 of 3088. « Previous 1 ... 121 122 123 124 125 126 127 128 129 130 131 132 133 ... 155 Next »
Important NoteAll messages are submitted by visitors to this web site, and represent their own personal opinion. They do not necessarily represent the views or opinions of Preloved. You use this information at your own risk. Preloved can not be held responsible for any damages or loss resulting from the use of this site. Please see our Terms and Conditions for more details. |
|||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Not a member yet?Why not join the fun for free! Members can sell their stuff completely free of charge, have searches prioritised for their local area, and lots more. Join for free | Member Log In
Are you a fan of Preloved?
If so, why not help us spread the Joy of Second Hand by joining us on Facebook. [more...] |
|||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||